luisss749
Mechanical
- Oct 5, 2015
- 16
Hi I'm working on a industrial exhaust ventilation system, the system consists of 4 branches that meet at a single point at the entrance of a dust collector, the operation of each one of these branchs can be combined at the end we can get 6 stages of work, after the dust collector we have a pipeline to the suction fan and a duct at the fan outlet.
The idea to separate all stages branches and merge them into a single point in the dust collector is analyze whether you can select a system fan or fans able to provide the flow and pressure required for each stage at any given time and get energy savings.
Air requirements for each stage are as follows:
Q = CFMs, SPfan = inWg
1. Q = 16950, SPfan = 10,390
2. Q = 2800, SPfan = 9,675
3. Q = 2800, SPfan = 9,786
4. Q = 2800, SPfan = 10,309
5. Q = 8550, SPfan = 8.220
6. Q = 11350, SPfan = 10,309
Using centriware 2.0 (flakt woods) i get the following fans for each stage:
P=Kw, n=rpm, eff.=%
1.- GTHB-3-090, P=26.43, n=1422, eff=80.1
2.- GTHB-3-040, P=4.22, n=3102, eff=77
3.- GTHB-3-040, P=4.28, n=3117, eff=76.9
4.- GTHB-3-040, P=4.54, n=3188, eff=76.2
5.- GTHB-3-063, P=10.27, n=1857, eff=83.8
6.- GTHB-3-071, P=17.06, n=1819, eff=83.6
As you can imagine i can't work with bigger fan with VF (surge problems), so i belive the solution is in using multiple fans array
I wonder, in your experience is this technically and economically feasible?
is this a common solution for industrial exhaust ventilation system?
wich iterature can you recommend to select/design (if feasible) a system with multiple fans? (Preferably with examples)
The idea to separate all stages branches and merge them into a single point in the dust collector is analyze whether you can select a system fan or fans able to provide the flow and pressure required for each stage at any given time and get energy savings.
Air requirements for each stage are as follows:
Q = CFMs, SPfan = inWg
1. Q = 16950, SPfan = 10,390
2. Q = 2800, SPfan = 9,675
3. Q = 2800, SPfan = 9,786
4. Q = 2800, SPfan = 10,309
5. Q = 8550, SPfan = 8.220
6. Q = 11350, SPfan = 10,309
Using centriware 2.0 (flakt woods) i get the following fans for each stage:
P=Kw, n=rpm, eff.=%
1.- GTHB-3-090, P=26.43, n=1422, eff=80.1
2.- GTHB-3-040, P=4.22, n=3102, eff=77
3.- GTHB-3-040, P=4.28, n=3117, eff=76.9
4.- GTHB-3-040, P=4.54, n=3188, eff=76.2
5.- GTHB-3-063, P=10.27, n=1857, eff=83.8
6.- GTHB-3-071, P=17.06, n=1819, eff=83.6
As you can imagine i can't work with bigger fan with VF (surge problems), so i belive the solution is in using multiple fans array
I wonder, in your experience is this technically and economically feasible?
is this a common solution for industrial exhaust ventilation system?
wich iterature can you recommend to select/design (if feasible) a system with multiple fans? (Preferably with examples)