Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Multiple relief valve - Relief load 1

Status
Not open for further replies.

asade

Chemical
Oct 19, 2010
65
In sizing multiple relief valves, should each valve be sized for full relief load? OR the Total relief load should be shared between the multiple valves?

Please, i need clarification.
 
Replies continue below

Recommended for you

Consider posting on the " Safety Relief Valve" forum.

Tell us more about the type of process and specifically what is being protected by the valves......

 
The total relief load can be shared between multiple valves.
Typically, each valve has at least 25% of the total required area.

At least one valve should have set pressure less than or equal to the vessel MAWP.
The other safety valves may have set pressure less than or equal to 105% of MAWP.
 
120% of the Total flow or one spare
(if you have 5 PSV each will be 24% of the max flow)

One with a lower set-point is a nice trick to overcome small bumps, but you need to make sure that your vent line stay atmospheric (otherwise you will cause back pressure on the others)

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor