MidwestStructE
Structural
- Mar 16, 2023
- 2
Due to IBC 2018 (and later) requirement, storm shelters are being built across the US when cities expand schools. The shelter typically has a concrete or precast roof.
There is a discussion about whether the uplift loads on this roof needs to be calculated as MWFRS or C&C, when the roof size exceeds 700 sq ft (ASCE 7-16 Section 30.2.3). I wonder what opinions there are on this on this forum?
The story so far:
IBC 2021 implicates ICC 500-2020 which implicates ASCE 7-16, which increases C&C loads relative to ASCE 7-10.
The difference in a typical uplift load is from ~170psf MWFRS to ~270psf average C&C (adding up the zone loads). (using the typical 250mph wind speed for tornado)
The minimum requirement for MWFRS in this case would be is a single space of > 700 sq ft with a solid concrete or precast roof.
As engineers, we are used to applying C&C loads to edges of metal deck roofs. These could bend upwards at the corners and edges, within the duration of a gust, and is a known factor. The same is not true for a 12" thick concrete roof.
The main issue is the connections, from the roof to the walls, and the walls to the foundations. No one is expecting a 12" reinforced concrete roof to flip up at the corner like a metal deck might, even under tornado loads. We can show that it won't. When we calculate the uplift, we are combining the zone loads to form an aggregate load in these connections. I think this factor alone proves that the localized C&C loads are not the issue for these roofs.
To me, this type of roof meets the MWFRS definition of ASCE 7-16 Section 26.2 - "An assemblage of structural elements assigned to provide support and stability for the overall building or other structure. The system generally receives wind loading from more than one surface." It receives wind loading from the wall surfaces as a diaphragm, and also vertical direct loads.
Opinions differ on this, and I think the ASCE maybe should clarify this, because this question clearly comes up a lot.
So, would the answer differ for a 2-way concrete slab vs a 1-way? If so, why? Or for a precast reinforced plank joined to an assemblage of planks by a topping, should the panel size be used, and again if so why?
There is a discussion about whether the uplift loads on this roof needs to be calculated as MWFRS or C&C, when the roof size exceeds 700 sq ft (ASCE 7-16 Section 30.2.3). I wonder what opinions there are on this on this forum?
The story so far:
IBC 2021 implicates ICC 500-2020 which implicates ASCE 7-16, which increases C&C loads relative to ASCE 7-10.
The difference in a typical uplift load is from ~170psf MWFRS to ~270psf average C&C (adding up the zone loads). (using the typical 250mph wind speed for tornado)
The minimum requirement for MWFRS in this case would be is a single space of > 700 sq ft with a solid concrete or precast roof.
As engineers, we are used to applying C&C loads to edges of metal deck roofs. These could bend upwards at the corners and edges, within the duration of a gust, and is a known factor. The same is not true for a 12" thick concrete roof.
The main issue is the connections, from the roof to the walls, and the walls to the foundations. No one is expecting a 12" reinforced concrete roof to flip up at the corner like a metal deck might, even under tornado loads. We can show that it won't. When we calculate the uplift, we are combining the zone loads to form an aggregate load in these connections. I think this factor alone proves that the localized C&C loads are not the issue for these roofs.
To me, this type of roof meets the MWFRS definition of ASCE 7-16 Section 26.2 - "An assemblage of structural elements assigned to provide support and stability for the overall building or other structure. The system generally receives wind loading from more than one surface." It receives wind loading from the wall surfaces as a diaphragm, and also vertical direct loads.
Opinions differ on this, and I think the ASCE maybe should clarify this, because this question clearly comes up a lot.
So, would the answer differ for a 2-way concrete slab vs a 1-way? If so, why? Or for a precast reinforced plank joined to an assemblage of planks by a topping, should the panel size be used, and again if so why?