kingtutley
Electrical
- May 11, 2007
- 49
I am doing conductor voltage drop calculations for a new subdivision. The secondary from my pad mount transformer is -probably- going to wind up at 350kcmil, but I need justification. I have 2 pedestals downstream from my xfmr. Each is feeding 2 single family dwellings with an estimated 10kW each. The first pedesdtal is 35' from the xfmr. Between the pedestals is 110'.
I have a max VD of 5% per NEC -- I understand that the NEC does not specify VD for service conductors, but since it specifies it for all others, I'm just going with that.
Now, the fun part. My question is not really about the calcs, but rather what values for R to use. The NEC specifies R in Table Section 9 Table 9 for AC conductors, but it also stipulates that these values are for the specified parameters ONLY. So, the parameters specify 3-phase. I am working on single phase 2-wire in schedule 80 pvc conduit. I have not been able to locate any derating factors for this, so I have used the values in the table. Is this justified?
I have a max VD of 5% per NEC -- I understand that the NEC does not specify VD for service conductors, but since it specifies it for all others, I'm just going with that.
Now, the fun part. My question is not really about the calcs, but rather what values for R to use. The NEC specifies R in Table Section 9 Table 9 for AC conductors, but it also stipulates that these values are for the specified parameters ONLY. So, the parameters specify 3-phase. I am working on single phase 2-wire in schedule 80 pvc conduit. I have not been able to locate any derating factors for this, so I have used the values in the table. Is this justified?