Hello,
We are installing a customer-owned 25 kV to 4.16 kV substation. This is a skid mounted system, and the only exposed energized parts are the tips of the high side transformer bushings. The substation will be outdoors, and will be protected by a 7 foot high fence with a locked gate.
Table 110.31 of the NEC (Minimum Clearance from Fence to Live Parts) requires 15 feet of clearance. Table 110.34(A) (Minimum Depth of Clear Working Space) requires 6 feet under Condition 2 (exposed live parts on one side, and grounded parts on the other side).
My question is 'What am I missing?" The site is tight for space, so I would like to go as small as possible, yet have a safe installation.
Note: Regarding the 4.16 kV end, Table 110.31 requires 10 feet to the fence, and Table 110.34(A) requires 5 feet under Condition 2.
Regards,
Podo