I need a VFD for 15 hp motor on 3/60/230 service. It needs a closed PID control loop option which is used primarily for HVAC applications I think.
We have a test fixture with a 15hp motor connected to a fan that we want to control. The fan will pressurize a chamber to a certain point and hold that pressure. We will change that setpoint often. There is a pressure transducer in the chamber telling us what the pressure is and outputting a 4-20 mA signal. This signal we want to feed right back to the VFD in the closed control loop.
I have found one from DanFoss, but it seems a bit expensive at $2800. Anyone have any suggestions on a certain manufacturer or good supplier?
Davey
We have a test fixture with a 15hp motor connected to a fan that we want to control. The fan will pressurize a chamber to a certain point and hold that pressure. We will change that setpoint often. There is a pressure transducer in the chamber telling us what the pressure is and outputting a 4-20 mA signal. This signal we want to feed right back to the VFD in the closed control loop.
I have found one from DanFoss, but it seems a bit expensive at $2800. Anyone have any suggestions on a certain manufacturer or good supplier?
Davey