Negative sequence currents - Generator

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
444
"Generator shall be capable of continuous operation at rated voltage and frequency on an unbalanced load at rated current but containing a 10% negative sequence component. Temperature limits may be exceeded by 5 ºC at this condition."

If I understand the above clause correctly, if the generator insulation is rated F/B, with a continuous negative sequence component of 10%, the temperature rise may exceed class B but will not surpass class F.

Is my understanding correct?
 
Replies continue below

Recommended for you

That depends on the nameplate rating. If the rated kVA is at a Class B rise, then it is saying that the winding temperature can exceed the Class B rise by 5 deg C.
 