robs68charger

Mechanical
Nov 12, 2009
13
0
0
US
I have a customer that has requested an expolsion proof motor on their metering pump. They also want an expolsion proof VFD to accept a 4-20mA signal. Does anyone know of a manfacturer of such a beast, or have any suggestions? I am almost thinking they should just buy a normal VFD and mount it in a safe location and run proper conduit and using fire stop instead.
Thanks
-Robs68charger
 
Replies continue below

Recommended for you

Gotta vote with Keith.

Put the VFD somewhere safe. Rigid conduit and a couple of seals is much less expensive than trying to contain and cool a VFD.

Good on ya,

Goober Dave
 