NESC or recommended distance between rail fuel loadout (explosive fumes) and substation?

Status
Not open for further replies.

apMechE

Mechanical
Aug 5, 2014
24
0
0
US
Have an existing substation and looking for numbers on how close a rail loadout of diesel and other fuels can be placed in proximity to it.
 
Replies continue below

Recommended for you

Beware that some municipalities and Electrical utilities recommend in excess of the NEC & NFPA clearances of at least 25 feet in all directions between fuel storage tanks up to 2,000 gallons and electrical equipment or energized lines. Smaller clearance could be allowed for small fuel tanks in a few hundred gallons.
 