lesmcw
Electrical
- Feb 11, 2004
- 4
Hi Guys: Could someone check this please. I am an electrician and was asked this question by another electrician and replied as follows, but want to make sure it's correct.
What is the current on the neutral on a three wire branch circuit, that is connected to a three phase 4 wire service. The three wire branch circuit has 12 amps load on each leg.
What is the formula for calculating the vector sum of these two currents.
It would be a Common Conductor when connected to two phases since it is no longer a Neutral. It would only be a true “Neutral” if connected to all 3 phases or as single phase since it only carries the unbalanced current.
To find the neutral current on a wye system the here is the formula:
(I dont have a square root symbol so the V and line are them)
______________________________________
\/ (AI^2 + BI^2 + CI^2) - (AxB)+(BxC)+(CxA)
written out, that would be: The square root of
(A phase squared + B phase squared + c phase squared) - (A phase x B phase + B phase x C phase + C phase x A phase)
Lets now give all three phases your value of 12 amps and find the Neutral load from the formula.
(12x12 + 12x12 + 12x12) = 432 - (12x12 + 12x12 + 12x12) = 432
432 – 432 = 0. The square root of 0 is 0. Therefore the identified conductor is actually a neutral.
With only 2 phases and a common (single phase) used, then:
(12x12 + 12x12 + 0x0 = 288) - (12x12 + 0x0 + 0x0 = 144) = 144
The square root of 144 is 12, so you see the Grounded Conductor carries the same current as the two phase conductors, and your answer is 12 amps.
What is the current on the neutral on a three wire branch circuit, that is connected to a three phase 4 wire service. The three wire branch circuit has 12 amps load on each leg.
What is the formula for calculating the vector sum of these two currents.
It would be a Common Conductor when connected to two phases since it is no longer a Neutral. It would only be a true “Neutral” if connected to all 3 phases or as single phase since it only carries the unbalanced current.
To find the neutral current on a wye system the here is the formula:
(I dont have a square root symbol so the V and line are them)
______________________________________
\/ (AI^2 + BI^2 + CI^2) - (AxB)+(BxC)+(CxA)
written out, that would be: The square root of
(A phase squared + B phase squared + c phase squared) - (A phase x B phase + B phase x C phase + C phase x A phase)
Lets now give all three phases your value of 12 amps and find the Neutral load from the formula.
(12x12 + 12x12 + 12x12) = 432 - (12x12 + 12x12 + 12x12) = 432
432 – 432 = 0. The square root of 0 is 0. Therefore the identified conductor is actually a neutral.
With only 2 phases and a common (single phase) used, then:
(12x12 + 12x12 + 0x0 = 288) - (12x12 + 0x0 + 0x0 = 144) = 144
The square root of 144 is 12, so you see the Grounded Conductor carries the same current as the two phase conductors, and your answer is 12 amps.