New AC Unit on a roof - Safe or not?

Status
Not open for further replies.

Zach Moussa

Structural
Oct 21, 2023
3
A new AC Unit will be put on a roof in my company and it's constituted of two units with the following specifications
Air supply Unit weight = 1.2 ton will be situated on a concrete footing above the concrete slab as show in the picture
Condensing Unit weight = 0.585 ton will be situated on a concrete footing above the concrete slab as show in the picture
Caspture_csplfl.png


So my design approach was this... Calculate total loads of concrete + unit for each unit and divide it by the total area of the concrete footing
concrete footing height = 0.5 meters

for the Air supply Unit + concrete weight = (1.2) + ( 2.03 (concrete area) * 0.5 (H concrete height) * 2.3 (RFT concrete density) = 3.53 ton
let's divide it by total Area = 3.53 / (3.07*1.75) = 0.66 ton/m2

for the condensing Unit + concrete weight = (0.585) + ( 1.51 (concrete area) * 0.5 (H concrete height) * 2.3 (RFT concrete density) = 2.32 ton
let's divide it by total Area = 2.32 / (2.55*1.3) = 0.7 ton/m2
...
For the sake of simplicity I assume that both of them exert an Extra 700kg/m2 load on the concrete roof...
--------------
Now to check for if the slab can withstand the load or not I redesign the slab with an Extra Dead load of 700kg/m2 repeated over the whole area of each slab

taking into consideration the both slabs have these specification :
-Slab thickness = 0.2 m
-Top reinforcement = mesh of rebar size 10mm every 15 cm ( 6.77 rebar/m both directions)
-Bottom reinforcement = mesh of rebar size 14mm every 15 cm ( 6.77 rebar/m both directions)
--------------
So Is this a logical approach or am I missing something?
one of my greatest concern is that I assume that the loads will be evenly distributed over the whole area of the footing and not as a line load underneath the beams of the footing
 
Replies continue below

Recommended for you

Generally the "ton" that mechanical people talk about is the amount of cooling power, it's not the weight. The weight is usually quite a bit less than the cooling power. I think I'm working on a 12.5 ton chiller and it's 1,060 lbs. (And yes, I know, a chiller is usually larger, don't ask me, it's what the data sheet calls the thing.)
 
@lexpatrie yeah I understand what you mean but those are the actual weights I extracted from the manual of each unit
 
Often with rooftop ACUs the loading problem comes from the snow accumulation loading in areas where snow is prevalent. Why do you need a concrete base; that's not common in these environs...

-----*****-----
So strange to see the singularity approaching while the entire planet is rapidly turning into a hellscape. -John Coates

-Dik
 
@dik we don't have snow at all here.... but yeah I have to use a concrete base for the getting the required level above the roof's finishing level for the ACU (finishing level + 0.15 m)
can you recommend any other alternative to the concrete base?

My current approach is to
-Demolish roof finishing in the required Area
-construct Concrete bases above the roof
-reapply roof finishing around the base
-Put the ACUs on the bases
 
Can you use load bearing insulation like DOW highload 60 or something similar? I don't know if you have to protect it from UV.


-----*****-----