leur2011
Electrical
- Jan 20, 2012
- 54
One (1) new 2000A bus, 1200A VCB, 3P, 3W, 60Hz, 50kA, 2sec vertical feeder section will extend each bus of my existing 4.16kV double ended metal-clad switchgear model PowlVac® manufactured by Powell Industries Inc. to feed the two (2) new 4.16kV, 1200A, 3P, 3W, 60Hz, 50kA, 1sec metal-enclosed motor control center. System grounding on the wye secondary side of upstream transformer feeding the existing 4.16kV switchgear is 400A at 10sec impedance low resistance grounding system.
My question if we can request from another manufacturer/vendor i.e. EATON, GE, Schneider to extend, supply and install the new feeder extension vertical feeder sections of existing switchgear. Or I miss something that will void the UL listing of my existing switchgear, and if there are other factor that will not allow me to ask other vendor except the OEM (Powell Industries Inc.) of my existing switchgear?
I need your expert opinion please. The project will be executed in the middle east.
My question if we can request from another manufacturer/vendor i.e. EATON, GE, Schneider to extend, supply and install the new feeder extension vertical feeder sections of existing switchgear. Or I miss something that will void the UL listing of my existing switchgear, and if there are other factor that will not allow me to ask other vendor except the OEM (Powell Industries Inc.) of my existing switchgear?
I need your expert opinion please. The project will be executed in the middle east.