If all none linear loads are connected phase-to-phase, will a wye grounded wye grounded transformer still pass neutral current? And to what degree?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
ANSWER: No, not if the load is connected phase-to-phase.cuky2000 said:QUESTION REFRACED: Does a balance non-linear load will produce current to flow into the ground from the transformer neutral point into the ground in a wye-grounded (earthed) transformer? Your thoughts.
Looking at it again, I agree with you.Mbrooke said:@warross: thats what I think, but it won't cause neutral current on the LV, just the primary MV.
I agree.che12345 said:I arrived at the following conclusion:
a) ...no current flowing through the earth to the earthed neutral ...
b) ...no current flowing through the earth to the earthed neutral ...
I disagree. Triplen loads from A to B will be cancelled by triplen loads from C to A, leaving none in line A to the transformer. Triplen loads from A to B will be cancelled by triplen loads from B to C, leaving none in line B to the transformer.waross said:Looking at it again, I agree with you.
A non linear load connected from A to be will cause triplen currents in both A and B secondary windings but there will be no involvement with the neutral.
They don't cancel in the secondary windings. They cancel in the phase-to-phase connected load before they get into the secondary windings. There are no zero-sequence currents in the lines to a phase-to-phase connected load. If there were, restricted earth fault protection would not work, as stevenal has pointed out.waross said:The triplen currents may cancel in the secondary windings but cancelled does not mean that they don't exist.