structeng2
Structural
- Apr 18, 2016
- 38
Hello,
I'm working on some equipment support/anchorage designs that are supported by steel platforms. We calculated the Fp forces based on ASCE7 Ch13 to determine the anchorage forces between the equipment and platform and then used Chapter 15 to analyze the platform structure itself (OCBF steel frame). For the seismic weight of the platform, we included the weight of the equipment.
There was a discussion in our group about how far the Fp force needs to be carried out into the structure. Chapter 13 forces are "...for their supports and attachments", but the question is how far do you follow the load path for the 'support'. (Let's assume that the equipment weight is less than 25% of the platform weight).
To highlight this, here are two extreme cases we discussed:
Case 1 - Assume we have a large building with a small piece of equipment anchored to one of the floors. It's very likely that after you get the Fp load through the anchors into the floor, the building forces control the rest of the building component/member designs after that.
Case 2 - Assume we have a smaller support frame with a decently sized piece of equipment. The Fp force may be the governing load for the equipment bolts, support beams, frame beams... maybe even the diagonal braces.
It feels like what we've seen in the industry is to just design the anchors or attachment points for Ch13, then the rest by Ch12 or Ch15. Curious what the input is from everyone here.
I'm working on some equipment support/anchorage designs that are supported by steel platforms. We calculated the Fp forces based on ASCE7 Ch13 to determine the anchorage forces between the equipment and platform and then used Chapter 15 to analyze the platform structure itself (OCBF steel frame). For the seismic weight of the platform, we included the weight of the equipment.
There was a discussion in our group about how far the Fp force needs to be carried out into the structure. Chapter 13 forces are "...for their supports and attachments", but the question is how far do you follow the load path for the 'support'. (Let's assume that the equipment weight is less than 25% of the platform weight).
To highlight this, here are two extreme cases we discussed:
Case 1 - Assume we have a large building with a small piece of equipment anchored to one of the floors. It's very likely that after you get the Fp load through the anchors into the floor, the building forces control the rest of the building component/member designs after that.
Case 2 - Assume we have a smaller support frame with a decently sized piece of equipment. The Fp force may be the governing load for the equipment bolts, support beams, frame beams... maybe even the diagonal braces.
It feels like what we've seen in the industry is to just design the anchors or attachment points for Ch13, then the rest by Ch12 or Ch15. Curious what the input is from everyone here.