Hi Everybody,
We have an existing power distribution from 115kV S/S, 20MVA xformer (115kV/4.16kV), a switchgear with 7SJ602 relays, 4160V feeders, 2MVA 4160V/480V xformers, and LV switchgears with micrologic 6A main CBs.
Based on the existing available fault at 115kV which is 2933 MVA We have already setup and commissioned our protective devices base on these parameters. We then have installed our emergency power system composed of 4- 1750kW, 4160V generators (syschronized). Since the available fault of this new system is very small compared to the normal supply do we need to adjust our existing settings? Probably the minimum fault during emergency is so small that the normal setting will be affected?
Any comments please....
We have an existing power distribution from 115kV S/S, 20MVA xformer (115kV/4.16kV), a switchgear with 7SJ602 relays, 4160V feeders, 2MVA 4160V/480V xformers, and LV switchgears with micrologic 6A main CBs.
Based on the existing available fault at 115kV which is 2933 MVA We have already setup and commissioned our protective devices base on these parameters. We then have installed our emergency power system composed of 4- 1750kW, 4160V generators (syschronized). Since the available fault of this new system is very small compared to the normal supply do we need to adjust our existing settings? Probably the minimum fault during emergency is so small that the normal setting will be affected?