cokeguy
Electrical
- Jan 29, 2006
- 117
We have a recurring problem in a couple of our A-B MCCs, where the main Cutler Hammer HFD3125L 125A breakers sometimes trip whenever a certain problem such as a short circuit or grounded line/motor trips one of the secondary MCP breakers. The loads are typically 3 HP standard 3-phase AC motors driven by combination starters with Cutler-Hammer HMCP015BOC 15A (mag.trip-only) breakers with corresponding A-B SMP-type thermal OL relays.
The question is, why would the individual breakers trip the main breaker if everything is correctly sized (apparently)? I´ve been told to switch to high interruptive capacity breakers to fix the problem, but in that case should I change the main breaker, the secondary ones, or all of them? (Ouch!!)
The rest of our MCCs are SquareD units with SquareD high interruptive capacity breakers and haven´t had those types of problems whatsoever, but I´m still not sure if the interruptive capacity rating of the breakers is the root cause of our problems. I would believe that even with standard interruptive capacity breakers, the secondary one should trip before the main one,
Any comments will be most welcome. By the way, the mag-trip point of the troublesome individual MCP breakers is set to its minimum, but it still trips the main breaker upon a shorted-motor type problem.
The question is, why would the individual breakers trip the main breaker if everything is correctly sized (apparently)? I´ve been told to switch to high interruptive capacity breakers to fix the problem, but in that case should I change the main breaker, the secondary ones, or all of them? (Ouch!!)
The rest of our MCCs are SquareD units with SquareD high interruptive capacity breakers and haven´t had those types of problems whatsoever, but I´m still not sure if the interruptive capacity rating of the breakers is the root cause of our problems. I would believe that even with standard interruptive capacity breakers, the secondary one should trip before the main one,
Any comments will be most welcome. By the way, the mag-trip point of the troublesome individual MCP breakers is set to its minimum, but it still trips the main breaker upon a shorted-motor type problem.