JohnBoy1
Electrical
- Apr 17, 2007
- 7
Has anyone out there come up on a situation where there is a building with mixed occupancy. I have one where the overall building is a "B" but within the same building there is also "M" and "A-3". The "A-3" is over 1000 load which requires voice-evac but the rest of the building would not require voice. My concern is there are areas that you could be hearing the voice message and the horns all at the same time. The city is using 2003 IFC. Also there is no one room in the four story building that has over 1000 occupancy, but combined comes to 1200. Any thoughts as to what might be required?