Reviewing a transformer spec (230/69/12.47 kV, 167 MVA single rating) and noticed the following verbiage:
"Class... ONAN/ONAN/ONAN or ONAN/ONAF/ONAF at Contractor's option"
Seems curious to me that they would suggest three stages of non-forced oil and air. The engineer that put this together is not available for questions, and I was wondering if anyone out there might suggest reasons why the ONAN/ONAN/ONAN rating was provided. ONAN or ONAN/ONAF/ONAF would seem the more accurate way to put this.
"Class... ONAN/ONAN/ONAN or ONAN/ONAF/ONAF at Contractor's option"
Seems curious to me that they would suggest three stages of non-forced oil and air. The engineer that put this together is not available for questions, and I was wondering if anyone out there might suggest reasons why the ONAN/ONAN/ONAN rating was provided. ONAN or ONAN/ONAF/ONAF would seem the more accurate way to put this.