Hello,

Usually, the reinforced bars have been anchored in a way that until the complete anchorage length is not developed, the bars do not contribute (see following figure):

111.png


But, I am wondering if it can be taken into account some type of contribution, in a linear way or other, since the anchorage starts to its end:

2222.png


Because in this case, with the same reinforcement the ultimate load can be a bit larger:
333.png


What do you think?

Any paper or guideline where this is explained?

Thank you
 
Replies continue below

Recommended for you

The capacity of partially-developed bars is usually ignored, I believe, out of convenience. Our girder analysis software checks sections with partially-developed reinforcement, if the actual end location of the bar and development length are input.
 
Section 9.2.1.3

(3) The resistance of bars within their anchorage lengths may be taken into account, assuming a linear variation of force, see Figure 9.2. As a conservative simplification this contribution may be ignored.

Thanks!
 