I am looking at a project that was not my design but is now mine to resolve.

Without having access to the early design decisions, it appears that the rooftop units are about 2 x as big as necessary. When the thermostat calls for cooling, it is satisfied pretty quickly, thus the compressor does not run all that long, so there is not a whole lot of dehumidification going on. Additionally, this is on the coast, so all the time the compressors are NOT running, the system is dumping a fairly humid mixture of outside air and un-cooled return air.

As I said, these are DX units, with 2 stage electric heat. To my advantage, they are 2 compressor units, so 2 stages of cooling.

Now in the good old days, I would have used a chilled water system with hot water reheat, cooled all the air down to 55F then reheated for comfort, thus yielding the sweetest, dry-est system in town. But not in these energy conscious days.

To obtain a dry space, I COULD replicate the good old days, driving the air cold then using those honking big EHCs to reheat. Not a good plan.

I COULD re-sheave, driving the cfm low, and the air cold to have the compressor run much more of the time...except...I believe I am going to be told by the manufacturer that the minimum acceptable cfm for the unit won't be low enough to match load/cfm/humidity to give a comfortable space and not damage the compressor. It will be better, but better probably won't be good enough.

So do you long-time DX guys have a magic bullet to shoot and put this high humidity problem down?
 
Replies continue below

Recommended for you

Is humidity in check with the outside air blocked off?

Take the "V" out of HVAC and you are left with a HAC(k) job.
 
It is much better, but since I am still doing almost no dehumidification, the answer is no. But it IS better.
 
Autofan

Take the "V" out of HVAC and you are left with a HAC(k) job.
 
Can you try a heat-pipe dehumidification system?

Are the DX coils split-face? Can one compressor then be locked out and the associated coil face be blocked off. Then reduce air flow.
 