Overturning due to settlement
rduke
Geotechnical
Apr 14, 2003
I'm looking for discussion on overturning for a mat footing. The site in question is south of Houston and has deep (30' investigated) saturated (H2O @ 3') clays with low strength. Torvane range 0.5 to 1.5 tsf., penetrometer range 0.75 to 2.5, UU's 0.6 to 1.8 tsf. The foundation is for a 50' to 75' tall (unknown at present), narrow vertical vessel. The footing will be lightly loaded, but I am concerned about overturning due to eccentricity. Any eccentricity could lead to differential settlements which would increase the eccentricity (and on and on) and I end up with the "leaning vessel of Houston". However, I don't want to specify deep foundations if it is not warranted. Should mat foundations be considered for this case?
The clays are not that soft. What do you have as far as consolidation data? This reminds me of Sarnia clays - but I'll need more data to confirm. To my knowledge we never had problems with our projects there (many oil refineries). Can you give some more data - consolidation, Atterberg's, expansive details, etc. of the clays? Thanks.
Just a little more info. clay: top 3'- LL=52, PL=18, PI=34. Below 3' - LL=34, PL=17, PI=17. Consolidation testing was beyond the scope, however, the secant modulus for 1/2 peak stress from the UU tests averages about 100 ksf. Also, the vessle may only be 40' tall, 8' diameter, 140 kips (fully loaded).