Hi Group,
For one of my projects, the contractor had gone ahead and placed a 16ft high masonry block wall on a composite metal deck (4" floor) on OWSJ. Note that the floor is not composite with the joist. Based on the analysis, I have determined that the joist will need to be reinforced. The floor is still standing because it has not seen the maximum live load and the new block wall is almost equal to the specified live load. Additional reinforcing is required for combined loading due to the new wall and the live load.
I have already completed the reinforcement design, however, I had to consider destressing the joist for the block wall load to eliminate pre-loading. I am trying to come up with the lift/jacking amount and thought about working with the theoretical deflection of a single joist due to the wall load. Note that the wall sits directly on top of the joist and runs parallel to the span. The theoretical downward deflection for the joist due to wall load is roughly 30mm over a 16m span. To me telling the contractor to lift the joist by 30mm seems a lot and I am thinking if I should be considering diaphragm action from the 4" composite metal deck (again deck is not composite with the joist). The joists are spaced at every 1.320m.
I am not sure how to model the deck stiffness. Based on a few elastic analysis runs, the floor slab seems to be distributing the load significantly if I use the bending stiffnesses of the deck from composite deck catalogs. To give you an idea, I am looking at deflections from 3mm to 10mm depending on how I model the deck in the model.
I am not sure what number to use for jacking at this point. I am concerned about providing a high value and ending up cracking the floor/wall above or potentially reversing the loading on the joist which will be terrible. Nor do I want to give them a smaller value that is not sufficient to fully unload the joists for the wall dead load.
Any thoughts on how to tackle this problem!
Thanks!
For one of my projects, the contractor had gone ahead and placed a 16ft high masonry block wall on a composite metal deck (4" floor) on OWSJ. Note that the floor is not composite with the joist. Based on the analysis, I have determined that the joist will need to be reinforced. The floor is still standing because it has not seen the maximum live load and the new block wall is almost equal to the specified live load. Additional reinforcing is required for combined loading due to the new wall and the live load.
I have already completed the reinforcement design, however, I had to consider destressing the joist for the block wall load to eliminate pre-loading. I am trying to come up with the lift/jacking amount and thought about working with the theoretical deflection of a single joist due to the wall load. Note that the wall sits directly on top of the joist and runs parallel to the span. The theoretical downward deflection for the joist due to wall load is roughly 30mm over a 16m span. To me telling the contractor to lift the joist by 30mm seems a lot and I am thinking if I should be considering diaphragm action from the 4" composite metal deck (again deck is not composite with the joist). The joists are spaced at every 1.320m.
I am not sure how to model the deck stiffness. Based on a few elastic analysis runs, the floor slab seems to be distributing the load significantly if I use the bending stiffnesses of the deck from composite deck catalogs. To give you an idea, I am looking at deflections from 3mm to 10mm depending on how I model the deck in the model.
I am not sure what number to use for jacking at this point. I am concerned about providing a high value and ending up cracking the floor/wall above or potentially reversing the loading on the joist which will be terrible. Nor do I want to give them a smaller value that is not sufficient to fully unload the joists for the wall dead load.
Any thoughts on how to tackle this problem!
Thanks!