Please see attached...
[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1481752061/tips/OWSJ_1_fikez5.pdf[/url]
Existing Pre-Engineered Metal Building (PEMB) Open Web Steel Joist (OWSJ).
Newly imposed HVAC RTU
I reinforce steel joists on a regular basis. But, I’ve never provided intermediate support for an OWSJ.
The client refuses to allow us to perform the necessary field work to reinforce the joist on the right end (17’-0”) of the joist as it is directly above their engineering offices.
While investigating the Sx and MOI to analyze whether we really need to reinforce, we had an idea to provide intermediate top chord support at the 23’-0” location.
Is there any reason this would not be acceptable?
If we follow through, do we sever the bottom chord below the intermediate support?
Other recommendations / cautions?
Thank you!
[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1481752061/tips/OWSJ_1_fikez5.pdf[/url]
Existing Pre-Engineered Metal Building (PEMB) Open Web Steel Joist (OWSJ).
Newly imposed HVAC RTU
I reinforce steel joists on a regular basis. But, I’ve never provided intermediate support for an OWSJ.
The client refuses to allow us to perform the necessary field work to reinforce the joist on the right end (17’-0”) of the joist as it is directly above their engineering offices.
While investigating the Sx and MOI to analyze whether we really need to reinforce, we had an idea to provide intermediate top chord support at the 23’-0” location.
Is there any reason this would not be acceptable?
If we follow through, do we sever the bottom chord below the intermediate support?
Other recommendations / cautions?