pinojman
- Oct 24, 2013
- 6
first post and hopefully, experts can guide me to find the answers.
problem started few weeks ago, routine test paralleling diesel engine with main turbine generator almost create shutdown to our plant. this test is weekly program, never find this problem before.
diesel engine 2x1.5 MW/ 6.6 kV ; main generator 7 MW/6.6 kV. normal load 5.5 MW.
synchronizing process running good, until the time when diesel engine orderred manual to take load from main generator. when load reach approx. 380 kW, suddenly load diesel generator each, increase almost max power it can handle (1.5 MW), it happened, even without manual ordered from speed faster in diesel.
already check for contact faster condition, all orders faster to woodward governor,and even restroke diesel actuator, all seems to be normal.
troubleshoot test repeated for almost 5 times, the problem still exist.
is there any spot, that we missed to checked? or problem begin from the main generator?
already replace the diesel generator with same parameter, problem still there.
thanks before.
thanks before.