Mztr45
Electrical
- Sep 15, 2023
- 8
Have two 3306 caterpillar 175kw generators with 2301 speed and load share controls and spm a synchronizers for each. When one of the generators is online and holding the load and second generator is running at rated producing power but not on the bus I have an issue when attempting to parallel. The instant I move the switch into parallel mode the online generator immediately ramps down in speed about 20 rpm and the oncoming will ramp up almost the same. This is confirmed watching frequency meter and rpm gauges.
These generators were paralleling and load sharing just fine a few days ago. Trying to nail down possible culprit where the problem is coming from. I'm thinking one of the synchronizers is on its way out and sending a garbage signal to the online generator even though it's not the oncoming generator. The same switch position is used for paralleling whether it's #1 to #2 or #2 to #1.
These generators were paralleling and load sharing just fine a few days ago. Trying to nail down possible culprit where the problem is coming from. I'm thinking one of the synchronizers is on its way out and sending a garbage signal to the online generator even though it's not the oncoming generator. The same switch position is used for paralleling whether it's #1 to #2 or #2 to #1.