I’m looking at an application where a local utility plans to add a second 20MVA transformer in parallel with an existing one in an existing substation. New transformer will be tapped from the existing incoming 138kv line with a new breaker and isolation switches added on high side. Secondary side will feed into an existing 13.8kv switcher lineup through an existing spare feeder breaker.
The secondary switchgear will have two transformers in parallel feeding the common bus without a bus tie and (4) load feeders connected to this common bus.
Each transformer will have its respective transformer diff protection with the mains and feeders in switcher having 50/51 protection.
Are there any issues with this application and is this something that is commonly done? Some questions that come to mind..
1) Increases short circuit level on secondary switchgear. Should not be an issue with (2) 20MVA units at 9.67%Z each proving aprox 20kA to 13.8kv gear.
2) Circulating currents....LTC’s on both units will need to have a master slave controller in order to avoid circulating currents?
3) Are there any potential issues with having a common bus with no bus tie? I’m used to switcher that has a bus tie and have not seen an application with two transformers feeding a common bus.
4) Other than the respective differential protection on each transformer is there any additional protection schemes that need to be considered for this application?
The secondary switchgear will have two transformers in parallel feeding the common bus without a bus tie and (4) load feeders connected to this common bus.
Each transformer will have its respective transformer diff protection with the mains and feeders in switcher having 50/51 protection.
Are there any issues with this application and is this something that is commonly done? Some questions that come to mind..
1) Increases short circuit level on secondary switchgear. Should not be an issue with (2) 20MVA units at 9.67%Z each proving aprox 20kA to 13.8kv gear.
2) Circulating currents....LTC’s on both units will need to have a master slave controller in order to avoid circulating currents?
3) Are there any potential issues with having a common bus with no bus tie? I’m used to switcher that has a bus tie and have not seen an application with two transformers feeding a common bus.
4) Other than the respective differential protection on each transformer is there any additional protection schemes that need to be considered for this application?