I have heard from a Japanese customer of mine that their utilities would run their distribution substations with two or more step-down transformers in parallell [put it another way, with the bus tie breakers normall closed]. He did not see any reason for concern, and yet could not name any advantage of such practice, other than the fact that if one transformer fails, and taken out by the differential relays, the loads would not see an immediate loss of power.
But, after all, transformers do not fail very often --- why such 'theatrics' for such a low risk ?
It seems to me that the disadvantages are :
[1] Increased short circuit current level, either putting system at risk, or necessitate more expensive and more capable fault interrupters.
[2] The risk of circulating currents running from one transformer to another, due to the slight differences in the secondary windings, even if the primary source is identical.
[3] Difficult and exacting differential protection required --- not only expensive, but one false move, you're dead ...
I hope to hear from utility engineers using this practice to enlighten me --- there must be something I missed in our imperfect info exchange --- one of us not communicating in his mother tongue.
I would like specifically to hear about the circulating current issue --- most utilities would not run closed loops at distribution except from the same transformer --- due to the concern of circulating currents. Wouldn't parallelling substation transformers create the same concern ? when the transformers are not perfectly matched ? Can someone cite IEC or IEEE standards on this issue ?
Thanks
But, after all, transformers do not fail very often --- why such 'theatrics' for such a low risk ?
It seems to me that the disadvantages are :
[1] Increased short circuit current level, either putting system at risk, or necessitate more expensive and more capable fault interrupters.
[2] The risk of circulating currents running from one transformer to another, due to the slight differences in the secondary windings, even if the primary source is identical.
[3] Difficult and exacting differential protection required --- not only expensive, but one false move, you're dead ...
I hope to hear from utility engineers using this practice to enlighten me --- there must be something I missed in our imperfect info exchange --- one of us not communicating in his mother tongue.
I would like specifically to hear about the circulating current issue --- most utilities would not run closed loops at distribution except from the same transformer --- due to the concern of circulating currents. Wouldn't parallelling substation transformers create the same concern ? when the transformers are not perfectly matched ? Can someone cite IEC or IEEE standards on this issue ?
Thanks