I am performing PD testing on short sections of sheath 22kV cable which has been factory tested to have <10pC at 22kV but I get very high PD readings 300-1000pC at 8.2kVwhich then decreases after several minutes to 2-3pC - does anyone know what effect is causing the decrease of the PD activity?
PD sometimes decreases prior to failure but this is new cable and the effect is repeatable by taking the cable to 9.2kV beyond inception then reducing and holding at 8.2kV