I have a problem when I did Per-Unit calculation. Under the same condition, I got two different P.U. results for the load current by using two methods, which doesn't make sense to me.
Condition: Terminal voltage is 10 kV, load power is 100 MVA, solidly ground Y system
Method 1: Let base voltage is 10kV and Base complex power is 100 MVA,
then Base line current is 100/(sqrt3*10) = 5.77 kA
in this case, the p.u. load current magnitude is 1 p.u
Method 2: By setting the same base voltage and base MVA as in Method 1,
load current magnitude p.u = complex power_p.u./(sqrt3 * line voltage_p.u.) = 1/(sqrt3 * 1) = 1/ (sqrt3) p.u.
My expertise is telling me Method 1 is right, but I just can't figure out what is wrong with Method 2.