I have been consulted to review the following situation. Here is what I have. A square pile cap 8'-6" x 8'-6". The piles are on a 4'-6" square pattern with 2' from pile to edge and 18" round concrete piles extending 4" into the cap. The pile cap is 3' thick with reinforcing 2" clear above the top of the piles. Apparently, the bar detailer did not pick up on the 180 degree hooks for the reinforcing which is 9-#8 ea. way. These caps were poured with this "straight" reinforcing. I have a set of plans and am just beginning to chase down the loads that are involved. W14 steel columns bear directly (grout) on top of the cap. I am at a loss as to how this slipped through the cracks, and the several sets of eyes that should have caught this. Is there any remedy other than tearing these out and replacing? I should add that 6-#8 and 1-#9 extend from the piles to near the top of the cap.