I am trying to understand and analyze a detail for a hanger support with seismic brace for a run of multiple pipes. The pipes are sitting on beams that are held up by threaded rods, coupled to anchors embedded in the concrete above. So far in my career I have not managed to fully wrap my head around the topic of seismic support for pipe systems, and it seems the literature out there is sparse, lacking detail, and usually manufacturer specific.
Looking at this detail, my first thought is that the pipe seismic forces from ASCE 7 chapter 13 are not applicable, because the pipes are not coupled to the supports, they just rest on the beams. Seismic motion in the concrete structure would cause the hanger itself to move, and the pipes would just bang around inside the beams and rods, no?
The other aspect to this is whether or not there will be any bending induced in the hanger rods. Let's say the pipes were all strapped onto the beams so they moved with the hanger under seismic motions. In that case, wouldn't the seismic force from the pipelines create bending in the rods, transferred through the beams, that would clearly fail the rods? With the pipes not being coupled to the beams, is this no longer an issue? The rods have such minimal bending capacity, I'm worried that even the impact from the pipes banging around and hitting the rods might cause too much moment, but I don't even know how I would go about checking that.
Your thoughts and ideas are appreciated.
Looking at this detail, my first thought is that the pipe seismic forces from ASCE 7 chapter 13 are not applicable, because the pipes are not coupled to the supports, they just rest on the beams. Seismic motion in the concrete structure would cause the hanger itself to move, and the pipes would just bang around inside the beams and rods, no?
The other aspect to this is whether or not there will be any bending induced in the hanger rods. Let's say the pipes were all strapped onto the beams so they moved with the hanger under seismic motions. In that case, wouldn't the seismic force from the pipelines create bending in the rods, transferred through the beams, that would clearly fail the rods? With the pipes not being coupled to the beams, is this no longer an issue? The rods have such minimal bending capacity, I'm worried that even the impact from the pipes banging around and hitting the rods might cause too much moment, but I don't even know how I would go about checking that.
Your thoughts and ideas are appreciated.