NFPA 291, Recommended Practice for Fire Flow Testing and Marking of Hydrants (2013) says:
"4.9.1 If a pitot tube is not available for use to measure the
hydrant discharge, a 50 or 60 psi (3.5 or 4.0 bar) gauge tapped
into a hydrant cap can be used.
4.9.2 The hydrant cap with gauge attached is placed on one
outlet, and the flow is allowed to take place through the other
outlet at the same elevation.
4.9.3 The readings obtained from a gauge so located, and the
readings obtained from a gauge on a pitot tube held in the
stream, are approximately the same."
My question is, what's the advantage to using a pitot tube and holding it in a flow stream? Wouldn't results be more uniform and accurate with the hydrant-cap-gauge method, especially across different individuals. (less prone to holding the pitot in the incorrect place, or turbulent flows, etc.)
I've read from two sources (NFPA 291 and Fire Protection Hydraulics and Water Supply Analysis by Pat Brock that the hydrant-cap-gauge method is virtually identical to the pitot tube, so I'm looking for any drawbacks that might exist for the hydrant-cap-gauge method as it seems to be the better option so far.
"4.9.1 If a pitot tube is not available for use to measure the
hydrant discharge, a 50 or 60 psi (3.5 or 4.0 bar) gauge tapped
into a hydrant cap can be used.
4.9.2 The hydrant cap with gauge attached is placed on one
outlet, and the flow is allowed to take place through the other
outlet at the same elevation.
4.9.3 The readings obtained from a gauge so located, and the
readings obtained from a gauge on a pitot tube held in the
stream, are approximately the same."
My question is, what's the advantage to using a pitot tube and holding it in a flow stream? Wouldn't results be more uniform and accurate with the hydrant-cap-gauge method, especially across different individuals. (less prone to holding the pitot in the incorrect place, or turbulent flows, etc.)
I've read from two sources (NFPA 291 and Fire Protection Hydraulics and Water Supply Analysis by Pat Brock that the hydrant-cap-gauge method is virtually identical to the pitot tube, so I'm looking for any drawbacks that might exist for the hydrant-cap-gauge method as it seems to be the better option so far.