PLC/HMI combo to use 2
tona2008
18
Hi everyone,
I was given the task of automating an oil heated press operation. The hot press needs two PID loops one to control the temperature and one to control the pressure. I have programmed the SLC 5/03 PLC before but only to control discrete outputs to open/close valves, alarms etc. Never dealt with analog signals. I need some guidance on which would be the combo PLC/HMI combo to use that will be the easiest to program and configure. Are there any PID modules on any PLC manufacturer that I can use to control the temperature and pressure? Can they be interphased to an HMI so that I can start the loops from an HMI screen? Does it have to be a PLC?
Any help will be appreciated.
Thanks,
I suggest you check out Opto22, they have inexpensive hardware and free software. I have used their product on a couple of jobs and found it works well. I have also used AB and found their monitors to be lacking.
Roy
There are really too many options to list, but for this application your best solution is probably a stand alone PID controller. There are a lot of options, but most of them work well, and you can get dual loop controllers from most maufacturers. I would check out yokogawa, eurotherm, omron, watlow, love etc. They will be heaps cheaper than any PLC/HMI combo, plus there is very little configuration to do, so you'll save on time on the design/programming side as well as the installation side.
Are these two loops (temp and pressure) interrelated? Maybe you should be looking at cascaded or other multi loop control strategies.
xJAyx
These 2 loops are part of a recipe. The temperature loop and pressure loops should be started simultaneously. This should be done on a single "cycle start" switch. I'm trying to prevent the operator from forgetting to start either one of the loops. This is why I'm trying to use an HMI where I can create a recipe and download it to the controller. With a soft internal switch start both loops at the same time. I know it can be done with a PLC but it requires a lot of programming.
Thanks for your suggestions,
Is this intended to be a stand alone system, or is it part of a larger system. By wanting to create and download recipes it sounds like a PC of some sort would be involved, to store the recipes.
A PLC such as the SLC 5/03 for example, has a built in software PID loop instruction, and just requires some analog I/O. It could also be used to store your recipe values, which could be accessed by a PanelView perhaps, removing the need for a PC.
PC based HMI and recipe control can get expensive, so unless it was part of a larger system, I'm not sure I would go that route.
NWBeaver,
Thank you for your reply, It is a stand alone system. This press is for use on our R&D department. This is why we don't want to spend too much money on this project. How difficult is it to program PanelView to be able to access this PID loop instructions?
Not difficult at all, the SLC PID instruction uses "N" registers. You would just need to create a Control Block of addresses such as N10:0 thru N10:22, for example.
In this example, the PanelView would then access N10:2 to read the Setpoint value.
The SLC instruction set manual maps out all the registers for you.
There are stand alone controllers that have recipe control, as well as hmi's that have built in recipe functions. I'm sure you could get a yokogawa 2 loop PID controller with recipe control.
