Golestan
Mechanical
- Nov 27, 2006
- 110
Please advise:
In small tenant finish-out projects in strip shopping centers. I have used ducted retun to the RTU return. A contractor is asking for design change into a plenum return scheme. Last time I did this I got in trouble because the RTU could not keep up with the cooling of the space. The air above the drop ceiling was just too hot. The building had R-30 roof insulation under the roof deck. So I am not comfortable the above ceiling (as plenum) return air.
Thanks,
In small tenant finish-out projects in strip shopping centers. I have used ducted retun to the RTU return. A contractor is asking for design change into a plenum return scheme. Last time I did this I got in trouble because the RTU could not keep up with the cooling of the space. The air above the drop ceiling was just too hot. The building had R-30 roof insulation under the roof deck. So I am not comfortable the above ceiling (as plenum) return air.