I am a mechanical engineer with an electrical problem. The power calculation using amperage, voltage, motor power factor and efficiency when combined with pressure readings on the pump performance curve gives a flow whiich is 20% higher (5000 GPM) than other measurements indicate.
The overall power factor for the plant site is corrected to .99 using a couple of large 18,000 Hp motors designed for the purpose but the power factor may not be .99 where the 700 Hp motor is connected. In fact it could be as low as 0.80
Can my horsepower calculation be the apparent power rather than the real power which actually used by the pump? I measure 96 amps, use 4160 Volts and interpolate for motor pf & eff from the test report.
I'm using the formula hp=1.73*E*I*pf*eff/746. The motor test report indicated that at full load the values are E=4000V, I=100.7 amps, Eff=94.8, Pf=78.9, Syn speed=900 rpm, Slip @ fL=1.43.
How would a supply power factor of 0.80 affect the Hp calculation. It isn't accounted for anywhere?
Any help would be appreciated.
The overall power factor for the plant site is corrected to .99 using a couple of large 18,000 Hp motors designed for the purpose but the power factor may not be .99 where the 700 Hp motor is connected. In fact it could be as low as 0.80
Can my horsepower calculation be the apparent power rather than the real power which actually used by the pump? I measure 96 amps, use 4160 Volts and interpolate for motor pf & eff from the test report.
I'm using the formula hp=1.73*E*I*pf*eff/746. The motor test report indicated that at full load the values are E=4000V, I=100.7 amps, Eff=94.8, Pf=78.9, Syn speed=900 rpm, Slip @ fL=1.43.
How would a supply power factor of 0.80 affect the Hp calculation. It isn't accounted for anywhere?
Any help would be appreciated.