Can someone shed some light on the possible or real effect's of inductive loading of a PM generator set that is running with loads that have power factors from as low as .20 pf to .36pf on average. And whether or not this would be the most likely cause of regulators going bad every 30 to 45 days this unit currently is on the fifth regulator.
The generator is the sole electrical power for a stone processing plant, There are two separate supplies to the plant both run through either variable frequency drive systems or soft start systems.
The max gen set KW is 1500 @ 480VAC. At the time of shut down today the load was approximately 1150 amps. The monitored DC field current output maxed out at 20 ADC.
This condition is happening randomly and once started it may run all day ok , 15 minutes or an hour before shutting down on a high voltage situation. I captured a reading of 668VAC.