We had a contractor put a fluke power quality analizer meter on our main switchgear. The info they recorded was that phase A on our three phase 480volt delta wye system was reading a power factor of 50% lagging and the other phases were reading phase B 80% and phase C 98% lagging. We have a square D switchgear with a meter on the gear that reads the power factor per phase plus voltage current KVA KV THD and so forth.. The readings on that meter read balanced with 80% power factor per phase A B and C. did the math for KV and KVA of the reading and all worked out to the display of PF.
We have no info from the contractor of KV or KVA of the phases. the question at hand is can his meter be correct? How can prove what meter is reading correctly. when i do the math using the meter installed on the switch gear it all works out. just need some advice to prove what we have and move on.