Hi Guys,

A basic question about output power from a generator:

If I have a three phase generator supplying:

Red 10.5A
White 6.4A
Blue 9.5A

..and I take (240v*10.5)+(240v*6.4A)+(240v*9.5A) will this give me total power output in KW or in KVA? And then how does one get the other format?

Thankyou in advance,

Cam
 
Replies continue below

Recommended for you

Assuming that the machine is connected 415V/240V so you are measuring line-neutral, then that is correct. To calculate kW you'll need to know the power factor of the load, and if the load is non-linear then you'll also need to know the value of the fundamental component of the current.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Thankyou very much.

Is there a formula to use for three phase that can make this calculation quicker?

For example 26.4Amps total. What equation can be used to calculate Total KVA?

Cam
 
For a balanced system
KVA=3*V*I, where V = line to neutral voltage, not line to line
KW=3*V*I*pf, where pf = power factor of system

For an unbalanced system, which is what you have, there is no shortcut.

EE
 