I think your "lack of consensus" is due to the fact this is a pretty broad subject. Later in the thread you finally stated what you're trying to do with the analyzer, but it still isn't clear exactly what you need. So probably a good answer to you initial question is "it depends".
What voltage and current levels are you trying to measure?
Are you trying to do logging/recording, like for power and demand studies?
Do you want to use the instrument for troubleshooting and service type work?
What kind of interface and/or reporting software are you looking for?
I am a small service type company, I own three different power quality type instruments,
A Fluke 1735, with flex CT's for up to 3000 amps and CT's rated at 10 amps for measuring CT secondary circuits, it does a nice job doing 7 and 30 day power studies, has some harmonic recording features and a fairly easy to use reporting software for rather simple reports. I don't think its on board display is very good, but when used with its software it does what I ask of it.
If I'm troubleshooting in the field I carry around a Fluke 435, has an assortment of CT's, has served me well on both low and medium voltage systems with the accessories I have. The recording is poor to fair, it takes FOREVER to download, and the software is a bit clunky, but I rarely use it for recording so it is ok for me. It has been rugged and reliable to date.
For more complex jobs I own a Fluke 1750, a testing company I used to work with had a lot of these and I had templates for reporting already made up. In most cases it does fine. I personally hate the PDA interface, think its a real piece of junk, and only use the PC via Ethernet cable. I like many of it features but on some parameters it does an averaging instead of the resolution I need for some current jobs.
I have rented a Dranetz HDPQ Visa unit many times in the last year, I test mainly generators with it and it meets my needs in several areas, so I am currently looking at replacing my Fluke 1735 and 435 with the Dranetz platform.
I have a customer who has both Elspec stationary and portable power analyzers, we had a number of installation issues with the stationary units that were the result of some poor documentation. The portable unit does measure EVERYTHING, but took a long time to drill down to the data needed. Of all the manufacturers I have dealt with on Power Quality equipment, I had the hardest time with these guys, for me it was a constant sales job and I needed technical help, so my view of them tends to be negative.
Another customer had a Hioki 3 phase unit, sorry I don't remember to model, that seemed to do a pretty good job but failed within a year, not sure of the cause, just pulled it out of the case and it didn't power up, even after charging the batteries.
I think where you are in the world has an impact on your choices, can you get it serviced/repaired/calibrated when needed. What if you want to add additional accessories, like current probes? Are they available and reasonably priced. How is the software? How about technical resources to help you use the instrument effectively, like online tutorials, good manuals, even YouTube videos?
LinkedIn has a couple of power quality specific groups that I have found helpful, I also work with a company in California that specializes in Power Quality and have rented equipment and taken training from them, so maybe that is an option for you as well?
Hope that helps, MikeL.