Paralleling two generators this size has a lot of drawbacks.
The act of syncrhonizing, matching phase and voltage as close as possible and being able to close the breaker of the oncoming unit quickly enough to assure you actually close while in phase can be done. Depends a lot on how stable your units are, do you have any ability to adjust voltage or speed and regulate it well enough to get a close that won't damage either machine?
OK, so you come overcome all the issues that come with synchronizing two units and get both breakers closed, now what? Is the speed and voltage droop the same for both units? Can it be adjusted? The ability to share both real and reactive power now becomes the issue. For larger units a number of options are available, for units this size, with fixed governors and voltage regulators, not much you can do. You might get lucky in certain load conditions, but it is highly unlikely you'll be able to properly share the load between the units without possible damage to either generator and possibly the loads.
I like the idea of either selling them and buy a right sized unit or split the loads. Unless you have something like the new Honda units that have the built in capability to parallel units, I think paralleing units this size is not feasible.
My 2 cents, Mike L.