I am at a bit of an impasse. I have a design/build project in which the general contractor wants to use a pre-engineered metal building as the frame and walls of a single story office. The architect (my client) has shown the use of gypsum wall board over metal studs which are supported by the building girts. I have been contracted to design the foundations only, but when seeing the detail posed the question as to if deflection had been considered. During a conference call today, I discovered that the wall girts are designed with a wind load deflection of L/90. Obviously this far exceeds what the gypsum can be subjected to without cracking. Have any of you run into this before? I am thinking of suggesting wall studs that span from top of stem wall to a beam (designed by me) meeting the wall board deflection criteria. The studs would be used to support the girts which are still needed due to the siding.
Does anyone have a better idea?