Is it possible to use Pre-insertion resistors in a 132 kV GIS CB.
The switching duty is for energizing a shunt reactor supplying a 100 km long 132 kV cable. The studies indicate a huge DC offset without current zeroes for approx 1.5 sec. Inserting a resistance can decay the DC component faster.
Alternatively is it possible to employ point of wave switching in case the GIS CBs are gangue operated ( not capable of single pole switching)?
The switching duty is for energizing a shunt reactor supplying a 100 km long 132 kV cable. The studies indicate a huge DC offset without current zeroes for approx 1.5 sec. Inserting a resistance can decay the DC component faster.
Alternatively is it possible to employ point of wave switching in case the GIS CBs are gangue operated ( not capable of single pole switching)?