Hi, I have a pressure reducing valve in sprinkler issue, my issue is when to install them in sprinkler system .
NFPA13 8.16.1.2.1 In portions of systems where all components arenot listed for pressure greater than 175 psi (12 bar) and the potential exists for normal (nonfire condition) water pressure in excess of 175 psi (12 bar), a listed pressure-reducing valve shall be installed and set for an outlet pressure not exceeding 165 psi (11 bar) at the maximum inlet pressure .
NFPA13 calls for it where it is overpressured.
Can i say , for PRV instalation of NFPA13, is it only allowed to be installed in such said case?
Other than that, is non-compliant? like, to reduce the pressure to desired level(The max pressure is not over 12bar or its rating pressure) . It seems a little vague.
Please share your view of this! we can lean .
FM has specifically specified this ,FM 0311 2.1.3 Do not use pressure reducing valves on sprinkler systems and hose connections where the static inlet
pressure is 175 psi (12.1 bar) (1210 kPa) or less.
To reduce /regulate the pressure , we have pressure-reduced deluge valve available, it is ok, if we have one ,or two deluge valves, we can use pressure -reduced deluge valve. While in Some case ,when there are more deluge valves (up to 10~20) in oil,chemical industres, to have one pressure-reducing valve at header would be cost effectly.
Thanks in advance!
NFPA13 8.16.1.2.1 In portions of systems where all components arenot listed for pressure greater than 175 psi (12 bar) and the potential exists for normal (nonfire condition) water pressure in excess of 175 psi (12 bar), a listed pressure-reducing valve shall be installed and set for an outlet pressure not exceeding 165 psi (11 bar) at the maximum inlet pressure .
NFPA13 calls for it where it is overpressured.
Can i say , for PRV instalation of NFPA13, is it only allowed to be installed in such said case?
Other than that, is non-compliant? like, to reduce the pressure to desired level(The max pressure is not over 12bar or its rating pressure) . It seems a little vague.
Please share your view of this! we can lean .
FM has specifically specified this ,FM 0311 2.1.3 Do not use pressure reducing valves on sprinkler systems and hose connections where the static inlet
pressure is 175 psi (12.1 bar) (1210 kPa) or less.
To reduce /regulate the pressure , we have pressure-reduced deluge valve available, it is ok, if we have one ,or two deluge valves, we can use pressure -reduced deluge valve. While in Some case ,when there are more deluge valves (up to 10~20) in oil,chemical industres, to have one pressure-reducing valve at header would be cost effectly.
Thanks in advance!