Proving Arc-Flash Compliance...

Status
Not open for further replies.

robbm

Electrical
Nov 2, 2005
56
A customer asked us to make sure our panels are Arc-Flash Compliant, and if they aren't - they told us we need to use a divider between the 480V and 120V circuitry. We've never had to deal with this issue, how/where can I find info on proving that our panel would be Arc-Flash compliant? Is it a matter of all the 480V devices being listed by the MFG as being compliant, or are there calculations and a certain rating in UL508 or NFPA79 to list a panel as arc-flash compliant?? thanks in advance for any help...
 
Replies continue below

Recommended for you

I don't think your client understands arc flash hazards. The arc flash hazard depends on the electrical system available fault current and impedance. This varies from plant to plant and their panel would have to be labeled for the specific installation.

I have not seen any standards for arc flash compliant panels. Are they making the request so there is no exposed 480 V energized components, so arc flash does not apply?
 
It depends on what country you are in, if in the USA, wbd is right, it is the end users issue, not the installer.
 
Try this

NFPA 70E
Standard for
Electrical Safety
In the Workplace
 