DETstru
Structural
- Nov 4, 2009
- 395
I have a two-way PT slab project currently under construction. The [genius] contractors decided to core a hole through 4 tendons in a 16-tendon band.
No visible damage to the slab.
After further investigation, it turns out that only 2 of the 4 were cut all the way through. The other 2 tendons each have 1 broken strand (of the 7 strands). After some reading, I believe the friction in the tendon along its length will transmit the tension from its 7 strands to the 6 remaining strands where the 1 strand is cut.
I intend to thread 2 new tendons for the 2 that are cut though. I can get away with only 14 tendons in that band.
My question is should I leave the other 2 intact or have them cut as well? Since the tension from 7 strands is now being held in 6, that's a 17% increase in tension in each strand. That's under the ultimate strength of the strand but it doesn't feel great and I don't want to risk a future break. I also don't know how much I really trust the remaining strands. It's not inconceivable that they were damaged in some way as well.
No visible damage to the slab.
After further investigation, it turns out that only 2 of the 4 were cut all the way through. The other 2 tendons each have 1 broken strand (of the 7 strands). After some reading, I believe the friction in the tendon along its length will transmit the tension from its 7 strands to the 6 remaining strands where the 1 strand is cut.
I intend to thread 2 new tendons for the 2 that are cut though. I can get away with only 14 tendons in that band.
My question is should I leave the other 2 intact or have them cut as well? Since the tension from 7 strands is now being held in 6, that's a 17% increase in tension in each strand. That's under the ultimate strength of the strand but it doesn't feel great and I don't want to risk a future break. I also don't know how much I really trust the remaining strands. It's not inconceivable that they were damaged in some way as well.