I have reviewed a number of forum discussions and posted guidelines regarding pump selection and pump nozzle sizing, and most appear to indicate that pump nozzle sizing is solely a product of the pump manufacturer's design and need not be considered in the system design and/or calculations for system TDH. However, perhaps this is a misunderstanding on my end.
Should not a reduction at the pump nozzle (assuming the system piping is larger diameter than the pump nozzle, which is typical) be specifically considered in system NPSHa calculations, considering pressure loss resulting from a sudden contraction at the pump and/or pressure loses from the increased pipeline velocity local to the pump connection may reduce NPSHa to a point where the pump is not usable due to cavitation (NPSHa < NPSHr)? In particular I would expect this evaluation would be essential when the pumped media has a high viscosity and sudden contractions could have large effects to the calculated NPSHa.
Should not a reduction at the pump nozzle (assuming the system piping is larger diameter than the pump nozzle, which is typical) be specifically considered in system NPSHa calculations, considering pressure loss resulting from a sudden contraction at the pump and/or pressure loses from the increased pipeline velocity local to the pump connection may reduce NPSHa to a point where the pump is not usable due to cavitation (NPSHa < NPSHr)? In particular I would expect this evaluation would be essential when the pumped media has a high viscosity and sudden contractions could have large effects to the calculated NPSHa.