I'm trying to select a pump for the hydrant valves of a warehouse. The warehouse is 170m x 114m x 14m, and the fire area is 208600 square feet.
Presumably, it's Type I construction, and by using "TABLE A-III-A-1", the fire flow equals 5000gpm. Because the area is fully sprinkler protected, can I reduce the fire flow by 75%? If so, the needed fire flow will get
5000*0.25=1250gpm
Also, for the sprinkler system, I have chosen a 1500gpm @ 9 bar fire pump, so can this pump supply both hydrant and sprinkler system?
Thanks.