Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Punching shear on pile cap

Status
Not open for further replies.

93albano

Geotechnical
Feb 1, 2023
3
DE
Dear all

I am designing a pile cap as attached using SAFE software.

I am getting failure of punching shear. How to solve?

Pile cap size: 7.5m by 10m, 1.5m thick;
Loads: 8800 kn vertical and 5000 kn horizontal;

Punching_shear_ynydiu.png
Mmax_lfjzoq.png
 
Replies continue below

Recommended for you

You can e.g., thicken the slab, add punching reinforcement, or increase the concrete strength.

PS. Are you using inclined piles? If not, 5000 kN horizontal load (almost as large as the vertical load) seems excessive.
 
The piles are vertical. Due to high lateral loads 9 pile group was adopted, this ensured that pile head lateral deflection is under 1% of pile diamter (1000mm).
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top