Narbij
Mechanical
- Sep 27, 2016
- 18
Hello community,
We have some "rig tanks" on site we use for temporary storage of liquids when cleaning our process tanks. We have used these tanks for years - I suspect they are API 12F tanks (pending confirmation). Assuming they are API 12F tanks and Design Pressure is 1 psi (16 osi) - the pressure relief device on the tank is currently set at 1 psi.
API 650 dictates that the set pressure for pressure relief needs to be below the design pressure to allow for accumulation and sufficient venting capacity at pressure. However, API 12F has no such provision - it simply refers to API 2000 where the only thing I see is Clause 3.6.2.2 which states that "it is often necessary that the set (start-to-open) pressure be lower than the design pressure of tank to allow for adequate flow capacity of the devices." - i.e. to allow for accumulation of vapour without exceeding the design pressure of the tank.
For API 650, this makes sense as the standard is for Welded Tanks for Oil Storage and can be of any size, either shop built or field erected. For API 12F, I am skeptical as they are (relatively) smaller, shop built tanks - I believe the set pressure is fine as is; however, I am getting resistance from another engineer saying that the device is not set correctly, i.e. the device should be set at a pressure below 1 psi to allow for 10% accumulation.
Anyone have any experience and/or comments about this? Am I incorrect in saying it is acceptable as is?
Thanks in advance for your help.
We have some "rig tanks" on site we use for temporary storage of liquids when cleaning our process tanks. We have used these tanks for years - I suspect they are API 12F tanks (pending confirmation). Assuming they are API 12F tanks and Design Pressure is 1 psi (16 osi) - the pressure relief device on the tank is currently set at 1 psi.
API 650 dictates that the set pressure for pressure relief needs to be below the design pressure to allow for accumulation and sufficient venting capacity at pressure. However, API 12F has no such provision - it simply refers to API 2000 where the only thing I see is Clause 3.6.2.2 which states that "it is often necessary that the set (start-to-open) pressure be lower than the design pressure of tank to allow for adequate flow capacity of the devices." - i.e. to allow for accumulation of vapour without exceeding the design pressure of the tank.
For API 650, this makes sense as the standard is for Welded Tanks for Oil Storage and can be of any size, either shop built or field erected. For API 12F, I am skeptical as they are (relatively) smaller, shop built tanks - I believe the set pressure is fine as is; however, I am getting resistance from another engineer saying that the device is not set correctly, i.e. the device should be set at a pressure below 1 psi to allow for 10% accumulation.
Anyone have any experience and/or comments about this? Am I incorrect in saying it is acceptable as is?
Thanks in advance for your help.