Hello,
I'm designing a simply supported rc beam(450x750dp) with effective span of 16.30 m.(pls. see attached loading and shear&moment diagram). If I used the criteria of "allowable span to effective depth ratio" it is failing. But when I consider the actual deflection = 27mm < L/250, it is OK. Would I go ahead since it is passing in the deflection criteria?
Also, Mrd = 0.167fckbd^2 =.167x40x450x670^2 = 1349.40kN.m > 801 kN.m(OK), it is passing with the Moment capacity against the design moment.
Any ideas will be greatly appreciated.
Regards,
I'm designing a simply supported rc beam(450x750dp) with effective span of 16.30 m.(pls. see attached loading and shear&moment diagram). If I used the criteria of "allowable span to effective depth ratio" it is failing. But when I consider the actual deflection = 27mm < L/250, it is OK. Would I go ahead since it is passing in the deflection criteria?
Also, Mrd = 0.167fckbd^2 =.167x40x450x670^2 = 1349.40kN.m > 801 kN.m(OK), it is passing with the Moment capacity against the design moment.
Any ideas will be greatly appreciated.
Regards,